Hi Ken,
Thanks for taking the time to help me. I'm new to the SLC5/05 environment and I'm still missing a part of the puzzle.
You indicated that I should only need 3 MSG commands to make a single drive work. In the example you provided, where does the speed reference and actual speed come into play? Are they part of the first write on line 0002 of your example?
Sorry to prolong this but I'm hoping to wrap this up so I can get home by Friday.
:confused:
Thanks to both of you for your generous help. It is much appreciated.
BLS
Foxhat, in the useful example coming from Ken, the rung 002 is used to write to the drive the Command Word and the Reference.
N7:3 must contain Logic Command Bits and it is moved to N41:0 by MSG write
N7:4 is unused and it is moved to N41:1
N7:5 must contain the Reference and it is moved to N41:2 in the drive
In line 001 he uses EEM to get the Logic Status and Feedback from drive:
N7:0 will contain the Logic status bits
N7:1 is unused
N7:2 will contain the Feedback
Instead of this new instruction (EEM) you may use another message, reading from N41:0 to N41:2 to get the same infos from drive.
- [font=comic sans ms,sans-serif]fuzzy logic[/font]
I have Woodward Controller EASYGEN-3500XT and Phoenixcontact make IO CAN-CUPLER part no: 2702230, Analog Input card: 2861412, Analog Output Card ...
39
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
98
126
I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
123
Or there is an alternative to this? I suppose there are many but I've only seen put/get Can you for example set up a new plc and connect it to an...
306