Is put/get necessary for communication between 2 PLCs?

plcnoob69

Member
Join Date
Jun 2023
Location
Nigeria
Posts
30
Or there is an alternative to this? I suppose there are many but I've only seen put/get
Can you for example set up a new plc and connect it to an existing scalance or profibus node, and have both PLCs read the same inputs? Or for example have one PLC raise outputs as signals to the other PLC?
 
You can, and should consider, multicasting when you have a large number of controllers as well.

Also, if you use PUT/GET, you must have some sort of heartbeat to detect if the other end is actually processing logic or simply turned on but in stop mode.
 
What is your PLC and FW and SW version?

Current Siemens PLCs support controller to controller comms as IO: I-Slave on Profibus, IDevice on Profinet. As you suggest, it maps IO memory in one PLC directly to IO memory in another PLC.

There is also a feature for multiple PLCs to read the same inputs from an IO rack, called MIMO, I think? It requires the IO device to support it, and not many do.
 

Similar Topics

All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
33
Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
14
Views
373
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
30
Views
1,146
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
261
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
Replies
1
Views
121
Back
Top Bottom