Communication between CompactLogix and Modbus protocol Devices
minaykha
Apr 2009
singapore
96
Hi, Anyone can help me?
I need to make compactLogix PLC program to communicate with the modbus device( SEL, Intelligent Motor Protection Relay ) over the modbus protocol.
Is Compact Logix support Modbus protocol without putting a Prosoft Hardware modules ?
I want to communicate compact logix PLC with the modbus devices without the use of any hardware module, by writing the read and write functions for modbus in ladder logic program.
I don't know where to start, Can anyone give me a guideline ? Thank.
Not that i am aware of. Ive asked myself why don't these big name manufactures make their own modules but i guess its a business decision or something else. Another thing you should also figure out is what kind of modbus protocol your modbus devices support, is it Modbus TCP/IP, RTU, etc.... I think prosoft is your best bet but you need to verify and understand what type of modbus protocol your field devices support first.
I very strongly recommend the Prosoft modules or another Ethernet/Modbus RTU bridge device.
ControlLogix and CompactLogix controllers do not have native support for Modbus RTU, Modbus ASCII, or Modbus/TCP protocols.
There are sample programs that implement Modbus via the serial port of the controller; they are included in the Sample programs that are installed along with RSLogix 5000.
This program is also available in the RA Knowledgebase as Answer ID # 42662:
https://rockwellautomation.custhelp.com/app/answers/detail/a_id/42662
In addition there is a document that describes this examples in detail, Rockwell Automation Publication CIG-AP129A:
http://literature.rockwellautomation.com/idc/groups/literature/documents/ap/cig-ap129_-en-p.pdf
While these example programs have been around for about 10 years, and are very well documented, I still don't use them because they consume too much memory and cannot be used with modern ControlLogix and CompactLogix that do not have RS-232 serial ports.
you will save yourself alot of headache if you use something like a red lion datastation plus or a digi one iap, that is if you are dead set against using the prosoft due to pricing.
I agree that using a module as other have suggested is a better approach, but they do have sample code to do modbus TCP on the Rockwell Sample code website, just search for "ControlLogix/CompactLogix Modbus TCP Program" on the sample code website.
Thank to you all for replies and info,
I looked into sample programs and found that it is too much complicated if compare to logix500.
i wondering why this type of application can be done easily with logix500 controller but not with logix5000 controllers.
I had an old project using Micrologix1400.
I used Msg instruction to communication with Modbus (TCP/IP) devices via Ethernet Switch.The program is simple and get the job done easily.
Now my boss want me to upgrade the same project by using Compactlogix and i found the different story.
No choice, Once i have no budget from my management for external modules, such as prosoft, i need to try with software code first.
Try my luck.:(
It's a learning experience, I suppose. MicroLogix has some built-in Modbus features and CompactLogix doesn't.
I use MicroLogix 1400 for just one of my machines for exactly this reason; there's another device that requires Modbus/TCP and it's included in the MicroLogix 1400 Series B controller.
Be sure to keep track of the time you spend testing this logic implementation and compare that cost to the hardware cost of the Prosoft module.
Hello Experts, I am building an application in Matlab (on my PC) which has a TCP/IP toolbox to allow me to connect to Ethernet enabled devices...
2,746
Hello guys, I'm new to this forum. I'm having problems to establish communication between a CompactLogix 1769-L30ER and a Mitsubishi VFD FR-F800...
4,346
Hi Experts. I need your help, I wanna communicate a MIcro850 with L19ER CompactLogix through Serial communication (Modbus RTU). I am using...
2,165
Hi experts, I have Panelview 800 Teriminal (version 4.012) connected to 5370 compactlogix L2 controller(1769-L24ER-QBFC1B). Through Ethernet...
16,449
Hi all I'm trying to establish communication between a L43 CPU and a PLC of another brand (B&R). At the moment I'm just trying to see...
5,296