Communication between Yaskawa and Rockwell
Yunchag
Sep 2009
Mexico
I have a question about communication between Yaskawa MP2600 and compactlogix of rockwell.
MP2600 have a ethernet port for EtherNet/IP and Modbus/TCP.
My question is : Is possible communicate this brands Rockwell and Yaskawa, if the answer is right, Will I need a OPC?
Not being familiar with MP2600 (is it an IEC version, by the way?), I can say that the whole reason Yaskawa supports Ethernet/IP is to be able to join the "Allen-Bradley world" and to communicate with the Rockwell PLCs.
So the answer is: yes, it most certainly can but you should look for the specifics in the manuals on Yaskawa web site or via their tech support.
Thanks for your answer, but I'm confused, when it is about communicate two brands, although the protocol is the same (Ethernet IP) i'm don't know if i have that use an OPC, when is an OPC used?
Thanks in advance
Yes, this can be done. Depending on the model of Rockwell PLC, you may have to use explicit messaging. There is no non-IEC version of the MP2600, so it is inherently IEC(at least in the US). Use OPC if devices can't talk directly to each other.
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
I have Woodward Controller EASYGEN-3500XT and Phoenixcontact make IO CAN-CUPLER part no: 2702230, Analog Input card: 2861412, Analog Output Card ...
47
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
112
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
150
151
