communication cable of proface HMI

Join Date
May 2007
Location
giza
Posts
153
Hello every body

This is communication cable of proface HMI to MPI port of Siemens S7 CPUs

from your experiance

Can anybody tell me why is the 9 pin in the middle!!!!!!!!!!!
What is HOUSING terminal for?????

Best regards

cable.jpg
 
The diagram is showing 2 PLC's connected to one Proface, you can add more just put the terminating resistor after the last one. If you only have 1 PLC put the terminating resistor on the only PLC.

And the 50 meters refers to the max length of the total run of the cables.

The Housing terminal is the metal housing of the DB-9 plug and receptacle. Most commonly used for ground and is shown with the cable shield connected to it. And notice the shield is only connected at one end of the cable.
 
Last edited:

Similar Topics

Dear All, I want to communicate s7 200 and proface, so please provide the pin diagram of communication cable. Thanks in advance.
Replies
2
Views
2,729
Does anyone know what software the IDEC FA-2J Controller uses? And what cable is needed to communicate? I can barely find any information on this...
Replies
2
Views
1,133
Hello guys, I need to change the configuration on an C200HW-PRM21 PROFIBUS-DP Master Unit and looking communication cable. Any one knows where...
Replies
0
Views
1,215
Hello everyone, From experience which is better for field use, 90 deg or straight and why? I a inclined to buy the straight one but started...
Replies
8
Views
2,112
hi i know that it require wire gaure 18 but i just want to know is that posible to use eternet wire as a io communication wire. (because it cheap...
Replies
2
Views
1,438
Back
Top Bottom