I hope everyone is having a good weekend.
I've got some remote racks that I'm trying to figure out how to check the status of the comms on the remote racks without causing a major fault on the CLX processor.
Here's a some screenshots of what I've got:
And I realize in the properties of the 1756-ENBT Module you have a checkbox that I've circled below:
Is there any status bits to monitor the comms to the module without faulting the processor? I've searched the AB knowledgebase and the manuals, but the only thing that I've found is this dad blamed checkbox that faults the CLX processor. Any help or insight you could provide would be greatly appreciated!
Thanks in advance.
Bobby
You need to use the GSV instruction to get the module status.
Look it up in the help files and follow the links to the module object.
The above is for a compactlogic monitoring enet comms to other processors, but the same is a for an ENBT
as long as FaultCode is 0, comms are OK.
Ian
Thanks Gerry and Ian.... I believe this was exactly what I was looking for. Your help is greatly appreciated.
--Bobby
Similar Topics
hi friends. i have PLC with 13 inputs , i want to give the status of these inputs to BMS server guy , he want to read the status through modbus...
Replies
4
Views
3,190
Hello All, I have an 1756-L72 ControlLogix Processor (V20) with an 1756-EN2T Ethernet card. I have added a Generic Ethernet Module to talk to a...
Replies
4
Views
4,811
Maybe someone here can help me or tell me this isn't possible. I have two CLX L71 processors with one HMI. They are for two slicers that are...
Replies
1
Views
2,577
hi , i am new guy here. i want to ask about missing Health block (%I%W) in NOE 0100.2. is there any way to get Health block status (just like NOE...
Replies
0
Views
1,630
Hello, I need to present the communication status of an operator panel with the PLC it is connected to. Basically a green light when...
Replies
4
Views
2,435
Back
Top Bottom