Communication Timeout between citect HMI and momentum
gherz817
Oct 2005
PHILIPPINES
58
I found out a problem between citect hmi and momentum plc. When i was in run time suddenly the citect screen got a #COM indicating
a Communication time out or no com at all. After 1 minute communication is ok. Why this happened? Anybody encounter this problem?
From the citect knowledgebase...
"The Momentum PLC closes socket connections after a period of no use that is greater than 10 seconds. This is a designed feature to maximise the use of the small number of sockets available for communications within the momentum.
However in an application a simple workaround should help; such as putting in a single alarm or trend tag that is read every 4 seconds or so, regardless of the opened page"
The complete article...
Momentum PLC and Citect Modnet Driver
Article number: Q3611
Created on: 22/03/2002
Product: Citect for Windows Versions 5.xx
[size=+]Summary[/size]
We are seeing hardware errors on Momentum PLC's. If we go off the graphic page for > 10 seconds and then go back to the said page the kernel will display an error like the following:
"Wed Feb 27 17:45:57 2002 01:33:21.059 Error: Channel offline, cannot talk
READ 0015 PORT1_BOARD1 MomLab 000017 16
Generic 000021 Driver 00000020 (0x00000014)
Citect then re-establishes communications but if I go off the page then the same happens again.
[size=+]Solution[/size]
Is there any way to increase the communication timeout value for devices in a FactoryTalk ME application? We have a communication path that...
1,158
I've got a Controllogix system that is doing a MSG Read from an SLC500 PLC and over the past week we have had multiple issues with the MSG timing...
5,710
Hi all, I'm stuck on this problem and I'm having a hard time finding information anywhere on it. I was hoping that some of you might be able to...
4,532
Hi Guys, Was wondering if someone would be able to shed some insight into a problem I have. Hardware wise I am running a SLC 5/05 processor...
7,277
having communication timeouts in rslogix! everything seems fine in RSlinx, but when i try to connect to my SLC 5/03 it starts to talk for about 15...
1,574