Communication with Panel view 600
Naik
Apr 2012
Pakistan
I am going to connect my PC with panel view 600 Model#2711-K6C14L1. But it is not giving communication. I have checked the cable it is serial straight cable. Kindly help me in this case of communication between panel and PC, Because i want get backup of panel view application. If is there any manual regarding my query kindly share with me.
Is your PV a "Modbus" PV? If so see manual below. ( page 19)
Which port are you connected to? The printer/AUX port? If so then was there a printer connected to it? Can you get to the configuration screen to check how that port is configured? It needs to be set for download/upload not for use for a printer.
What software are you using to connect to the PV?
Coomunication Between PV 600 & PC.
Yes we are the printer/AUX port for connection, But no printer is connected with this network. I am using Panel Builder 32 version3.8 to connect with PV.
Naik Muhammad
I&C Engineer
PanelView 600 configuration
I had problems connecting to a PV600 also. There are manual links on some other threads. Before you go much further check the configuration - press the < and > keys at the same time. This was how I changed the printer port to enable communication.
Naik Muhammad
I&C Engineer
Well then the procedure on page 19 of the manual I posted above should work for you.
Let us know or provide screen shots if you are still having trouble.
Panel view CAT number 2711-K5A2 Getting fault "612 No active mode found on network" Not sure if connected correctly and channel configuration is...
2,028
Good morning, I would have a question to ask you. I have a Micrologix 1100 to which I have to connect a PanelView C300 in ethernet. I have...
2,087
problem in communication between micrologix 1200 & Panel View 600 Plus by serial DF1 Hello Friends i have to do communication between micrologix...
6,625
I had recently repaired a panelview plus 1250. the older firmware version of panelview was 5.00.04.55 (CPR 9). The repaired panelview came with a...
4,723
Hi, i have panelview plus 700 hmi i dont have the hmi backup. i am trying to upload the backup from hmi i am getting the below message the...
1,629