Compact Logix Ethernet
T Gibbs
Jun 2012
Morristown, TN
406
I'm having issues with a compact logix on ethernet. This is my first go around with RS LOgix 5000 so I'm still learning. I have a L33-ER with 8 I/O cards in the rack. I then have 5 1734-AENT ethernet point I/O modues. I have set the thumbwheels on the AENT to 011-015. I set my controller IP to 192.168.1.10. It still won't communicate. Does AB require that I use their patch cables or will any straight through cable work? What am I missing?
After you set the thumbwheel switches did you cycle power to the AENT adapter modules?
The adapter reads the thumbwheel switches only when you cycle power to
determine if the switches are set to a valid number.
Regards,
George
After you set the IP address and can successfully ping them, you have to go into the properties tab in the I/O tree, switch to the "chassis size" tab and set the chassis size in the module.
Well done, but...
T Gibbs said:
...Why does AB have to make **** so complicated?
It's a pity they don't provide technical help on such matters?...
...Oh wait, they do?...
50474 - 1734 Point I/O Inputs and Outputs Do Not Respond
Access Level: Everyone
...and detailed manuals for diligent users to read up on?...
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1734-um011_-en-p.pdf
...Chapter 4 - Configure the Adapter for Direct Connection in RSLogix 5000 Software
I have a CompactLogix 5280 a I am trying to figure out which of the Ethernet ports are A and B. Not finding it in the manual and this is a new...
1,209
Dear all Can any one guide me for mapping in compact logix in RS Logix 5000 which I will be using MOXA MB Gate 5105 for converting Ethernet IP to...
1,570
I have a 1769-L32E Compact Logix processor. I am using the EtherNet port already. I want to know if I can use the serial port to connect to...
1,904
Hello everyone, to get straight to the question, I have done simple programming with digital inputs and outputs but I have never programmed a PLC...
3,591
Hello all! Have an existing 1769-L18ERM-BB1B V28. with full expansion to 8 modules 1--1734-OB8 and 7--1734-IA4. According to IAB this can not be...
1,887