...First I gave the same Panel ID for the both HMIs. I also tried with different Panel Id(i have to make sure this) i was still getting a com error code.
Sorry, I got called away to a problem...
Your L32E is node address 0, which looks correct for SlaveID. So slave ID should be set 0 in both HMI projects. Panel ID 2 looks ok for the 507's node address. However, I would advise you to use sequential node addresses on a DH-485 network, just for performance reasons only. This is not essential, it just helps speed up the token passing when the token has to poll unused node addresses.
Because the L32E is 0, you would have to make the HMIs nodes 1 and 2, but, it's also good practice to leave node address 1 free on a DH-485 network in case a device is new or defaulted. So I would skip passed 1 and start at 2.
Also, the MaxID is set to 2 in your screenshot. This means you are telling the HMI that there are only 2 devices on the DH-485 network, when there is actually 3. I think this should be set to 3 min or 31 max? This is another performance setting for when there are only a couple of nodes used out of the possible 31. MaxID is the equivalent of Max Station Address in the L32E serial port settings, which is at the default 31.
So I would make the nodes...
L32E = node 2
HMI 1 = PanelID 3
HMI 1 = SlaveID 2
HMI 1 = MaxID 3 or 31
HMI 2 = PanelID 4
HMI 2 = SlaveID 2
HMI 1 = MaxID 3 or 31
Try that and see how you go?
Regards
George