I am attempting to use the 1769-ASCII 2 Channel Module with a CompactLogix 1768-L43 Controller to connect to two AccuRange AR 700 lasers, with one laser connected to each channel of the module. The serial port of the controller is connected to the host computer. However, I seem to be unable to have the module's ports be recognized in the RSLogix 5000 program. For example, if I use an 'AWT' instruction to Channel 1, I recieve an error code which indicates that the port does not exist. I am confident that the module has been mounted correctly, and the module has been configured to match the laser specifications. Is there some other option which I am missing?
Thank you,
JWRem
I actually found the solution. The 'ASCII' commands like ARL, AWL, etc only apply for the serial port on the controller. To use the module's serial ports, you need to mess around with the various bits within the controller tags.
See the example in the manual 'Compact I/O Ascii Module'
The 1769-ASCII module does not provide additional User Mode ports for use with the ASCII recieve/transmit instructions in the CompactLogix (AWT, AWA, ARD, ACB, etc).
Instead, data is received and transmitted by the module using the I/O tags that are defined when you configure the module in the I/O tree of the CompactLogix.
One of the example projects that gets installed with RSLogix 5000 is called "Example for 1769 ASCII Module.ACD". It should be a good supplement to the User Manual for getting started with this module.
Good day all. I'm trying to create a new project with a 1668-L43 CompactLogix controller. When I try to create new, That controller is not in the...
1,902
Absolute newby here. Also new to PLC. But I am a seasoned Electronics and Computer Tech. Helping to get my buddy's machine back up and running...
2,156
Hi. We have CompactLogix PLC 1768-L43 with two 1768-ENBT modules. One ENBT is configured for local network with VFD's and HMI, default IP is...
1,841
This is taken from a previous thread: "With the 1768-L43/45 processors, there is another buss where communications cards can be added to the left...
2,402
PRODUCT SERVICE ADVISORY 1768-L43 CompactLogix Controller Series A, Catalog Revision A01, Firmware Revision 15.07 Ref: ACIG 2007-02-001 Date...
15,175