conductors passing over DIN rail
rpoet
Jun 2008
New York, NY
536
Other than company spec and/or best practice, is there any code or standard (UL508A, etc...) violation if circuit conductors pass over DIN rail?
Example: Relay is mounted on DIN rail, and its socket has terminal screws on both sides. Wire duct is only on one side of relay. Can wires from the "other" side pass over the DIN rail and back into the wire duct?
Practically, I think we've all done it, especially in retrofit and repair situations. I have a colleague asking if there is a code/standard prohibition against doing so. I believe it looks sloppy and one should try to plan better especially in new panel builds, but it's sometimes unavoidable.
Thoughts?
Thanks,
rpoet
I’m not aware of any restrictions like that. UL508a does specify clearance for bending wires though. With small gauge and plenty of clearance it is a non issue most times.
Hello all. So... last night this crept in to my mind. PLC lead times... Seeing that there is a lot of talk about the shortages producing...
30
12,937
I have a branch circuit with the following motor and drive: Motor 1.1hp 480VAC VFD 1.5kW Normal Duty 2.0hp NEC 430 seems to suggest that I...
19
4,853
Hi all, I'm trying to get a bom together for an R&D project. I have modbus devices that require 355mA for power plus communications. Does anyone...
1,311
Im currently in a situation where our prefabricated copper twisted shielded pair (18awg) instrumentation cables are coming up short...
2,672
Because of 3 or 4 posts with errors on this subject, this US National Electrical Code admonition needs repeating: NEC Handbook Article 430.22...
5,813