hi everyone,

I'm wondering if there is a way to connect a CPU314 IFM with only a MPI connection to a ET200S IM151?

I'm used to do it with profibus DP communiction, but this cpu has only a MPI connection (X1 port) and no profibus port.

Is there a way to do this?

thanks for your replies.
 
It is possible. You have to add a CP342-5 if there is a free slot. If not all 8 slots are used, then it is possible. You then connect the IM151-1 via the CP342-5s profibus port.

But I dont like that the result will be based on a lame and obsolete CPU, the 314IFM.

How many I/O are use in the existing setup ?
I am thinking that a better solution is to switch the CPU to one with at least a DP port, or to go to ET200S with an IM151-8 CPU and Profinet instead of Profibus.
 
thx Jesper for your reply.
Regarding the very small amount of IO's, it's indeed probably the best solution to switch to another cpu.

this thread may be closed.
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
309
I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
103
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
Replies
2
Views
121
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
351
What has been your experience with year over year price increases on your Tech-connect service contracts? Is it up to the distributor? 30% seems...
Replies
5
Views
290
Back
Top Bottom