Connect expansion rack

hoejinkim

Member
Join Date
Aug 2012
Location
Oregon state
Posts
23
Hi
I am working on connecting DL205(D2-06B) to expansion rack(D2-09B-1)
How can I connect them each other?
(- do I need another power source or just get the power from Base PLC?
- do I need cable to connect? I have D2-EXCBL-1)

thanks
 
A D2-06B cannot be used as an expansion base. It lacks the connectors. The D2-09B-1 is will work fine.

Basically you will need:

1. A new D2-06B-1
2. Either a D2-250-1 or D2-260 CPU
3. A D2-CM module
4. Two D2-EM modules
5. A D2-EXCBL-1

The second base can potentially be powered from the same source as the first assuming there is enough amperage draw available and it is fused correctly or has an appropriately sized breaker.

All of this information can be found in the D2 User Manual, part number D2-USER-M available at AutomationDirect.
 

Similar Topics

Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
Replies
0
Views
68
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
353
I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
122
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
Replies
2
Views
154
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
374
Back
Top Bottom