I am writing my thesis for a company and I have to connect a GEFRAN H5000 humidity sensor to a B&R PLC. The information of the sensor says that if you connect it to a TLC555C oscillator, the signal frequency represents the humidity. But is it possible to 'read' frequency's with a plc?
thanks a lot,
I'm rather new in the PLC world :)
Brecht.
In a word no. it sounds like the 555 will give out a pulse train dependant on the humidity (voltage of the sensor) I assume this humidity device must give out a voltage of some kind to control the ocillator chip.
Most plc's have analog cards varying from mv, 0-10v 0-20ma, or 4-20ma.
If you could find out what the actual output is then it may be possible to convert it to a 0-10v or 4-20ma signal.
I don´t agree with Parky.
Frequency is the number of pulses over a certain time.
If you have a digital input that can read up to the max frequency, and if you know the frequency for 0% humidity and the frequency for 100% humidity, you can read the humidity with a digital PLC input.
Simens for example as a level transmitter with a frequency output: 3RG6013-3RS00
130hz you will need a high speed input or a counter card.
the resolution will not be very good a better solution is a sensor with 4-20ma or 0-10v output
Just take another sensor that gives you a signal 4-20ma or 0-10V , keep it simple
Johnson Controls has that type of sensor ,or other brands whatever
Most capacitive sensors are only really good to 1% RH anyhow, so a 130 Hz signal would likely have sufficient resolution to display the reality of RH.
Sure, lots of device will read out to 2 decimal places, but how real is the reading? With RH, not very likely that it's real.
thanks a lot guys!
the reason i chose a capacitive sensor, was his reaction time.
My problem has been solved without using a relative humidity sensor (leakage detection).
thanks !
cheers,
Brecht
176
97
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
109
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
341
What has been your experience with year over year price increases on your Tech-connect service contracts? Is it up to the distributor? 30% seems...
288