Connected Components Workbench question

Join Date
Mar 2023
Location
Wyoming
Posts
4
So I'm using CCW to program a panel view and this is not my first I have done many. My Problem is I get an error message that I have never seen before when I validate my program. The Error is: Location Tags Description is Tag# (used within the Screens text is not valid. What does this mean I have never seen this before I'm confused. Please send Help!
 
Could mean you have a tag used or defined in a hmi screen and it is missing in the tag database
 
I dug through the whole program and everything had a tag assigned to it. I finally found where the problem was it was in a text box that had a tag associated with it to display a variable. Thanks for the reply I'm moving forward again.
 