Connection Simovert with DriveMonitor via Profibus

snab

Member
Join Date
Aug 2011
Location
Ukraine
Posts
7
Dear colleagues, I need your help! There is a need for parameterizing Simovert VC in DriveMonitor on Profibus. But in menu in DriveMonitor can not select a connection via Profibus (the menu item is not active). Only connection via USS is available. The compendium is written that the choice of the connection via Profibus is available only if you operating DriveMonitor under Drive ES. But I installed Drive ES. Please tell me, what could be the problem?
There are currently installed such software: 1) PCS7 v7.1 SP2; 2) Drive ES Basic V5.5; 3) Drive ES PCS7 V6.1 SP2; 4) Drive ES Simatic v.5.4 SP1.
 
You need to insert your drives from inside Simatic Manager.

Create a project then-

Insert>Program>Drive>
Be sure your bus address is set (P918 on drive)
and your PG/PC interface is set

The profibus selection in Drive Monitor will now be active (bold)
 

Similar Topics

I am working on a project to back up software for a number of machines for a client, and am having problems connecting to SIMOVERT MasterDrives...
Replies
12
Views
3,212
I'm having a hard time either remembering or figuring this out. I have a PLC program and the associated HMI program. I know what this means...
Replies
4
Views
117
Hello, I have an issue where I want to simulate an Siemens HMI panel, through NAT connection to a PLC. I have the possibility through extended...
Replies
5
Views
204
Hello guys i'm working with an s7 1200 plc with an ET 200S expansion module. The problem is that i can't find the plc when searching in the...
Replies
1
Views
118
I have got an Rockwell PLC 1769-L36ERMS . I have assigned a IP address to it . But every-time I Reboot the PLC it looses Communication to my PC...
Replies
1
Views
114
Back
Top Bottom