Control panel wiring

pauly

Member
Join Date
May 2002
Location
South Wales,U.k
Posts
244
I would like to get some feedback from the forum regarding control panel wiring and in particular segregation of wiring.
I happen to be part of a business who insist on using double trunking to separate 24 volts and mains. By mains I mean 110v and above.
All cable is tri-rated cable
I can understand comms/data cable segregation and high power cabling.
I have yet to find any guidance from any European standards either.
All input welcome
 
I usually used the system of putting two main vertical conduits on each side edge of the panel, the right one for the power cables and the left one for signals and 24V.

The terminals at the bottom well segregated with the power on the right and the 24V and signals on the left.

In the horizontal ducts it is not possible to achieve total but close segregation.
 
Wiring must have an insulation rating greater than the maximum voltage present in the trunking.

In a nutshell, this is the minimum requirment.

Generally tri rated has an insulation rating of 600v.
 
My suggestion would be to try and understand the requirement in its entirely.

If standards exist in the country of use then that is the place to start. For example, a lot of the systems I have been involved in are subject to AS3000 (Wiring Rules) and AS4024 (Safety Of Machinery Series), which have sections derived from a number of IEC's, EN's and ISO's (Type A, B and C). Additionally, you need to comply with any EM regulations and directives that may, for example suggest that certain cables need to be earthed or shielded, or certain signals can not be influenced by external sources or generate interference externally.

There are hardware or equipment specific requirements for items like sensitive measurement equipment, or vision systems, and then there are customer specific requirements for industries like mining, utilities, food/beverage, defence and construction. Typically these will be on an installation by installation basis.

You need to look at the installation subjectively to determine what is and isn't appropriate, and in the case of segregation; there could be a great many reasons to do it.... Or it could be that one person said that it's how they did it in the past at X organisation (Whether that is a requirement in your own organisation or the customer's/site's request), so really there may be no reason to do it at all.
 
Last edited:

Similar Topics

Can anyone recommend a book, publication or website for learning to create control panel wiring diagrams? I know there are standard electrical...
Replies
1
Views
1,602
Hi all, Wondering what is the preferred method for running power around the panel. For example when building a panel if you have 24VDC from a...
Replies
22
Views
8,062
hi friends, i need some material regarding control panel wiring concepts. plz give me ur hands to me. thanks regards jdram
Replies
2
Views
3,585
Hi, If building a control panel in a 508a shop, when does it become a motor control center and fall out of scope for labelling under 508a? More...
Replies
1
Views
387
Does anyone know of a good person/company that could troubleshoot an electrical problem in a control panel in South Carolina - tomorrow? If...
Replies
9
Views
2,205
Back
Top Bottom