Troubleshoot Control Panel Problem in South Carolina

Summerville, SC

Contactor coil burning everytime it's switched on, and it takes down 24VDC power supplies.

As a guess at the issue: is it using a 24VAC coil?

Your description aligns with this as a root cause. I may or may not have learned this firsthand…
 
Last edited:
Ok wow... here is what I got back from the client:

1) The fans first contactor had a weak spring in the relay

2) The second contactor had a 24v AC coil

3) The third contactor was just right

In point #2 a contactor with 24VDC was ordered!
 