I have a project using 480 to 120 vac control transformer. I also need to run one small 1.5 amp 120 vac motor. Has anyone upsized and used the control transformer to do this?
While you don't provide much detail in your description of the system, Good practice would be to use a separate transformer for motor loads to avoid motor operation influencing the control system.
just my .02
Thanks for your .02 I do appreciate it. I am working to find out if I will even need to run this small motor when the other 6, 480vac Motors run. This small motor may only run during Change Over for positioning.
Code wise, the transformer size has to be 125% for the motor FLA, plus whatever for the controls load, I'd use (2) seperate transformers as the motor will make your power supply dirty. If you still want to use one transformer, use a 480v to 120/230v secondary and place the motor on one leg and the controls on the other, fuse your loads on the secondary side in addition to the primary 480volts side, ground your neutral point and you can always use a surge suppressor if your controls leg if they are electronic,
Motor "affecting control system", "make your power supply dirty", etc. Where do you guys get this stuff?
The electric company uses one transformer to power your house, and possibly some neighbors.
NCIVAN, upsize, fuse properly, and relax. It will work fine.
Make sure one side of the output is grounded for safety.
Hi everyone, I'm having issues with a control transformer (120V to 24V). Our conveyor system is set up to protect against product jam-ups...
2,909
I thought I had an easy question but there seems to be a lot of variations on this site as to the proper way to fuse a control transformer. I...
2,411
I read this article http://www.acmepowerdist.com/pdf/Page_64-65-68.pdf and did a sample control transformer sizing. Given: a contactor with 192...
3,043
Last night I came across a weird situation at the plant. A hydraulic unit wasn't running, but it should have been. Closer inspection revealed...
8,799
I
I want to connect a control transformer to my Ac unit. I need to connect it to 220 Volts AC. The one I have has 4 wires to connect to. White as...
23
4,846