I read this article
http://www.acmepowerdist.com/pdf/Page_64-65-68.pdf
and did a sample control transformer sizing.
Given: a contactor with 192 inrush VA and 29 Sealed VA (steady state)
According to the table in link above, correct transformer size would be 75 VA if I select the inrush VA 211 from the 95% "secondary voltage" and 40% "power factor" column.
Do you think the sizing is right? 75VA more than 2 times the steady state VA requirement of the contactor.
What would happen to the contactor if the control transformer secondary voltage drops down to 50VAC (120VAC nominal) during inrush?
http://www.acmepowerdist.com/pdf/Page_64-65-68.pdf
and did a sample control transformer sizing.
Given: a contactor with 192 inrush VA and 29 Sealed VA (steady state)
According to the table in link above, correct transformer size would be 75 VA if I select the inrush VA 211 from the 95% "secondary voltage" and 40% "power factor" column.
Do you think the sizing is right? 75VA more than 2 times the steady state VA requirement of the contactor.
What would happen to the contactor if the control transformer secondary voltage drops down to 50VAC (120VAC nominal) during inrush?