Hello,
I have machine that's currently running a Micrologix 1400 PLC controlling an AB Powerflex VFD via Ethernet/IP. We want to replace the VFD with a Yaskawa GA800 VFD but I'm trying to figure out how to setup the MSG instructions to work with the Yaskawa.
The attached screenshots show how the MSG write and MSG read are currently setup for the PF drive. We're only sending the start/stop/reset logic and speed ref to the drive. We're only reading run/fault status and current speed from the drive.
Does anyone know what I would need to set for the Class, Instance, and attribute values to make it work with the Yaskawa? I have the Yaskawa document AN.AFD.22 that shows how to setup the explicit MSG but its a little confusing to me. Link here-> https://mobile.yaskawa.com/delegate...D.22&cmd=documents&documentName=AN.AFD.22.pdf
EDIT: never mind, this program they sent me is already setup for the GA800 VFD so that answers my question.
Hi Everybody, this may be one for you motion control guys. We have been tasked with interfacing some Yaskawa drives into a project where the...
264
Hi! I'm currently trying to implement my first AB Control Logix PLC program using Yaskawa P1000 drives (7 of them).. I haven't managed to make...
1,977
I'm looking for a PLC solution to control multiple variable frequency drives at one time. I have a testing setup that uses Yaskawa V1000 VFDs to...
5,064
Hello. I installed 7 Yaskawa V1000 Drives along with the Yaskawa SI-EN3 comms cards. I was able to follow the steps from the Yaskawa web site when...
5,871
Dear All, I have to control the pressure of a liquid with a Yaskawa V1000 inverter. The inverter is connected with Profibus to a 317-2-DP CPU...
2,510