Controlling Siemens variable frequency drive
Pandiani
Apr 2005
Tz
718
Hello guys,
by examining one STEP 7 program that is used for controlling VFD micromaster drive I came accross one part which is particulary interesting to me.
Code:
 	  L	 DB1.DBW1 			  //control word
 	  T	 "MW12"
 	  L	 "control_datas_DR".DR_setpoint	//setpoint
 	  L	 1.638400e+004
 	  *R
 	  L	 1.000000e+002
 	  /R
 	  RND
 	  T	 "MW14"
 	  L	 "MD12"
 	  T	 "DR_send"				  //output word
I need someone more experienced to explain me what is happening. If I understand correctly, something like this is happening.
Setpoint that is read from some other location and which is in % (0-100%) is converted to number between 0 and 16384 and send to drive.
This opens two types of questions:
1. Why number 16384 is used? Is it standard for all Siemens' drives?
2. What exactly is a control word? Is it standardised, or a programmer is defining it according his particular needs?
Looking forward to your answers...
Here is the control word, you will notice the 16 bits for each control function.
In my experience this is very similar to all drives that support a PPO profile for profibus too. As far as the 16 bits for speed reference, it is 32767, the MSB bit is used for a sign (FORWARD OR REVERSE)
Try to send the drive -16383 and you will see the drive reverse directions.
The Masterdrive can support 32 bits (thats why I asked the question regarding the exact drive, the phase Micromaster should have been a clue for me :) )
Controlword
Hi Pandiani
I think it is 0-4000 HEX. It is on Danfoss.
ControlWord is 16 bit for control the drive eg. start,stop, rev,
ect.
I have not been working with Siemens, but i think Danfoss and Siemens works more and less the same.
Banker
BTW. I will try the filter you have made next week look very good.
More help again please... See the picture. I want to make the rectangle visible when Mr_Zr_ToggleSwitch is 1, and make it invisible when 0...
2,482
Hi all, I received a request from a customer, and I am doubting if this is the correct way of doing things. We have a Siemens 1500F PLC, with...
1,960
Hi all, I've hit a bit of a brick wall and need some help. I'm currently trying to get a Siemens S7-1200 PLC to talk to an Eaton DE1 Drive I'm...
3,686
Hey guys! Im using step7 v5.6. I have s7-300 on my desk, connected to vacon v20 i installed the opte5 card in the v20. So now im trying to...
18
4,406
Hey Guy, I would like to control the (attached) DC motor drive with my S7-1500 PLC through an HMI. when i say control i mean only the speed...
2,235