Controllogix Alarm & Event - Event Creation
Jieve
Feb 2012
USA
274
Hello all,
I am trying to detect certain events (motor started, setpoint changed, etc.) and have these sent to the HMI using a FactoryTalk View SE local station. PLC is a Controllogix 5572, Studio 5000 v33. Reading through the Alarm & Event Configuration Manual, they seem to make no distinction between the two (alarms and events).
As a test, I set up an ALMD instruction with severity 1. It shows up a TRIP (as it is a digital alarm I suppose), in the default green color. I see under the Alarm Window Configuration, under the "states" tab, that events should actually show up in blue text, so I'm assuming there is a proper way to configure them.
So how do you properly configure an event in FactoryTalk View SE and Studio 5000?
Any help would be much appreciated. Thanks!
I am looking for possible solutions for an alarm paging system that would meet the following requirements. - Alarm source is a 1756-L71 Processor...
4,288
I have an application were I need to pass the alarm tag and it's associated timestamp to kepserver. The timestamp must be generated in the plc. I...
2,409
Is using a GSV, Class MODULE, Attribute FaultCode Not Equal to Zero a sufficient alarm for when the Remote Rack drops off of the network?
3,788
50
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
86