I am working on a controllogix PLC and creating a new Tag ( Alias for a local 32 way Output ) , when I go to create the tag using the popup box, and assigning the Alias to the local Output it shows me that the output I want is been used, but when go directly to the local tag and do a cross reference it not been used, and look like the last three on the card are the same.
 
I am working on a controllogix PLC and creating a new Tag ( Alias for a local 32 way Output ) , when I go to create the tag using the popup box, and assigning the Alias to the local Output it shows me that the output I want is been used, but when go directly to the local tag and do a cross reference it not been used, and look like the last three on the card are the same.

The cross-reference facility can be used "By Logic", "By Tag", and "Tag Hierarchy" - look at the bottom of the Cross-Ref screen for the tabs....

If you don't see any "Logic" references, there could still be "Tag" references, e.g. someone had previously set-up an alias, and never used it.

You might even discover "the last three on the card" are aliased by tags called "Spare_nn", lol, I've seen it happen....
 
Yes thanks I did find it and you where right it was an obsolete I/O someone had remove from program but didn't delete and old tag.
I appreciate you time and help :)
 
that spare_nn has caught me too, not sure if it considered good practice or not I have always just left spares untagged

My thoughts exactly, no need to tag anything you aren't using or referencing.
 

Similar Topics

I'm new to AB and I'm running into a lot of things people tell me can't be done in AB that actually CAN be done, so I thought I'd ask here if...
Replies
3
Views
5,003
Hi, How I can use in the TASK#2 a tag created in the TASK#1? I try with alias task but when you create an alias tag you can only refer to tags in...
Replies
3
Views
6,870
Hey guys, I am programming a ControlLogix processor and have an alias question. Can I make an alias that points to only part of a DINT? I would...
Replies
7
Views
4,895
I'm trying to integrate a Beckhoff IPC with a Controllogix PLC. There is some documentation, on the Beckhoff website, on how to do a PLC-PLC comms...
Replies
0
Views
112
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
Replies
1
Views
110
Back
Top Bottom