ControlLogix alias
Anderman123
Feb 2007
WV
Hey guys,
I am programming a ControlLogix processor and have an alias question. Can I make an alias that points to only part of a DINT? I would like an alias that points to the first 8 bits of an output (and then another to the second 8 bits).
Thanks for your help.
Not directly, as far as I can tell. Since you can't directly make a single byte in a DINT it's own tag you can't alias it.
However, you could copy (COP) the DINT to a SINT array and alias the to the elements in the SINT array with other SINTs.
Keith
Hello Anderman123;
This is from a RSLogix5000 program we use:
As you can see, the individual bits that make up the INT-type tag are not available for aliasing (greyed-out).
If feasable, best would be to make a small logic that would move the 8 LSB bits into a new tag (AND the value with 0F and copy); then move the 8 MSB bits to another tag (BSR times 8, copy); the new tags can be aliased.
Hope this helps,
Daniel Chartier
Edit: Kamenges, your solution is a lot simpler than mine Congrats!
Keith,
Rather than doing it that way (unless I have some absolute reason to want to define up a bunch of alias tags), make yourself a UDT of 32 bools. You can give each member a unique name and comment. Then create an instance of that UDT, and COP the DINT to it. I use that all the time for breaking down status bits coming from drives (and for sending command words).
Keith
You see, that's why they don't let me go out and talk to customers. I get way too focused on the question. I ASSUMED (BAD!!! BAD!!!) that the OP was referring to a single DINT and wanted only the SINTs. It is more likely that they have a larger number of related DINTs. As rdast stated, in that case a UDT would be more efficient from a development standpoint, and it is basically self-documenting.Keith
Group,
I have some old 1771 racks with 2 slot addressing. I was hoping to divide up the bits for each card without any logic.
Thanks for the Ideas.
You won't be able to get this done without logic.
In ControlLogix, I would recommend looking into the BTD instruction(bit field distribute), for simplicity, and it is easy on the eyes. You can then take a DINT, specify which bits to send to your desitination tag. You can even put both instructions to move a DINT to 2 SINT's on a single rung.
You are stuck with some logic, but, er, so?
If it bothers you, put it in a subroutine somewhere so you don't have to look at it all the time.
A single COP instruction per I/O module really isn't bad. I typically buffer all my I/O anyway, so this would land naturally in the "Scan_Physical_Inputs" / "Update_Physical_Outputs" subroutines.
Anderman123 said:
Group,
I am working on a controllogix PLC and creating a new Tag ( Alias for a local 32 way Output ) , when I go to create the tag using the popup box...
2,310
I'm new to AB and I'm running into a lot of things people tell me can't be done in AB that actually CAN be done, so I thought I'd ask here if...
5,004
Hi, How I can use in the TASK#2 a tag created in the TASK#1? I try with alias task but when you create an alias tag you can only refer to tags in...
6,870
Hello everyone, has anyone managed to communicate Twido with Controllogix using the Ethernet connection?
42
130