controllogix analog module online range change
lucifer
Nov 2003
52
hi guys,
can anybody tell me what do u do when u need to change the transmitter fitted to controllogix & want to update the range & span settings online i.e. scaling parameters in module setting ..........i think u need to restart the plc or atleast module to get new settings effective
comment..........
The scaling for the controllogix analog modules can be done while online. Just open up the properties section for the module and select the configuration pulldown menu. Select the input you want to rescale and input your new scaliong data and you're done. If you are online when you do this the program will ask you if you want to inhibit the module prior to it accepting the changes.
Actually, it is my experience that it depends on the module you are asking about. Many of them require that you use the SSV (set system variable) instruction to get the module to accept and start using the changed variables. You can ususally find examples in the appendix of the module's user manual.
Darren
Hi I'm trying to change the scale in a analog Input module in the module while online. I got a warning saying something like Module changes could...
2,063
Hi Guys, I've been doing some experimenting in the shop and im hoping someone will be able to point me in the right direction. I was able to...
1,962
Dear all, I a have issue with 1756-IF8 Module , I reading some Air pressure and temperature analog values from this card , I have total 4 Analog...
3,018
Hello Everyone, I'm trying to use a ControlLogix 1756-IF16 Analog module to input some 4-20ma flow sensors. The sensors are single ended 2 wire...
2,157
Is there a way to see what the actual field signal value is going into each channel of the Analog Input I/O card 1756-IF16? In other words, I...
3,664