4-20ma device with a ControlLogix Analog Module
MudShark
May 2017
Oklahoma
Hello Everyone,
I'm trying to use a ControlLogix 1756-IF16 Analog module to input some 4-20ma flow sensors.
The sensors are single ended 2 wire type but the configuration for the module only has a 0-20ma setting.
Can I still use this module with the 2 wire analog sensors?
If so how do I scale the min max?
AB 1756-IF16 CONTROLLOGIX 16 PT A/I MODULE UPC: 61259817178
This is all the info I have from the build sheet.
I can check the module label in the morning for a catalog number.
I don't recall any selection other than 0-20ma in the properties configuration tab.
Yea, sorry I saw that you had posted the catalog number already. If it is set to 0-20 by default you will want to put an offset in. I'm not completely familiar, but looking in that manual, starting on page 193 should get you pointed in the right direction. Let us know what you find out.
Curious basic question about multi-signal transmitters, if I have a device that gives a 4-20mA feedback signal (say position or level) I can use...
2,286
Ok, so I have 2 boxes with separate power supplies they are going to be about 300 to 400ft apart. the Main Box as the PLC in it with the Analog...
19
5,402
At our waste water treatment plant we have several 4-20ma pressure transmitters. My job is to check calibration of all of our level devices the...
19
4,789
have a question. I have about 18 machines that involve feeding fabric, glue, etc. and there is a infeed table that I will build that will have a...
2,419
Hello all, I am looking at configuring the hardware of a system. We need a 4-20mA sourcing outputs and analog inputs. I have two options, two...