Hello all,
I am looking at configuring the hardware of a system. We need a 4-20mA sourcing outputs and analog inputs. I have two options, two different modules, a 4 channel 4-20 input module and a 4 channel 4-20 sourcing output module. Or, a 8 channel 0-20 input / 4-20 sourcing 4 channel output combo module. The cost of the combo module is less than the other two combined and it will allow me to go to a smaller rack saving even more money. My question does it matter that the combo card is 0-20 in not 4-20? All the input devices are 4-20.
Thanks,
Micheal
Hi
I often use 0-20 cards for 4-20 items as if the unit is disconnected I get a - value so I know the unit is faulty or been disconnect.
Once your scaling is set up right I cant see any trouble.
What are you going to be connecting
Donnchadh
Thank you for the help. We will be using a pressure transducer and a Signet Conductivity meter.
I figured it could be corrected/offset using thr scaling in the PLC, but it has been awhile.
Micheal
Curious basic question about multi-signal transmitters, if I have a device that gives a 4-20mA feedback signal (say position or level) I can use...
2,309
Ok, so I have 2 boxes with separate power supplies they are going to be about 300 to 400ft apart. the Main Box as the PLC in it with the Analog...
19
5,493
Hello Everyone, I'm trying to use a ControlLogix 1756-IF16 Analog module to input some 4-20ma flow sensors. The sensors are single ended 2 wire...
2,178
At our waste water treatment plant we have several 4-20ma pressure transmitters. My job is to check calibration of all of our level devices the...
19
4,810
have a question. I have about 18 machines that involve feeding fabric, glue, etc. and there is a infeed table that I will build that will have a...
2,423