ControlLogix and S7-400 Communication via Ethernet
Maharu
May 2011
Rizal
Guys can you help me on how to use MSG instruction in CLX to send a message to S7-400? Please give me the steps on how to do it, starting from the configuration of MSG in CLX down to the necessary blocks and ladders to be created in Step7 programming.. Thanks!
Hi there,
Anyone correct me if I am wrong..
ControlLogix can use EtherNet/IP or Modbus TCP as communication protocol.
S7-400 can do Profinet and maybe Modbus TCP. So as I see it, if no additional hardware is installed, you will need to configure the 2 PLCs to use Modbus TCP, where one will be master and the other slave.
The easiest way is probably to use a gateway between the 2 PLCs, such as EtherNet/IP slave to Profinet slave:
http://www.anybus.com/support/support.asp?PID=301&ProdType=Anybus X-gateway
//Patrick L
Hey friends..i am using Vijeo Citect SCADA software...can anyone please tell me how to Log Data using Microsoft Access Drivers...???
Nobody will be able to help you much because you haven't indicated that you have the necessary hardware to connect the two.
I believe this is called highjacking a thread.
You need to re-post this in a new thread.
You are likely to get better responses if you take the time to explain more about what you are doing and what you have sone yourseld to this point.
I have seen ethernet to Profibus converters.
I was on a Rockwell seminar just recently and they had a new module which has been designed specifically to 'talk' to Siemens PLC's but how it works I don't know. It might be a good idea to give your rep a call
Mark
Is there an availaible exemple somewhere or an ''how to doing it'' I have 5 micro 1400 cpu to be controled by 1 controllogix using ethernet/IP...
9,605
Hello everyone, I'm having an issue trying to get a messaging instruction to work. I'm trying to get some data from a Micrologix 1400 to a L83E...
18
6,231
I have 5 systems that include a ControlLogix PLC and a Micrologix 1400 PLC. I need to connect these two via ethernet. I want to have two inputs on...
1,789
Hey everyone, I've recently returned to the automation world after several years absence. I have been tasked with changing the network scheme of...
2,067
Hi, I usually work with siemens and the TIA portal but a customer has a series of cabinets I do with Micrologix and Panelview Plus 6, I haven't...
2,237