Controllogix I/O ladder question

OZEE said:
You were getting those failures because of comm problems (noise, connections, etc.) - not because of the RPI. Changing the RPI only changed how often the errors were encountered. Reread what Ken wrote -- I marked the important clue... I would almost bet that you have at least one of the following:
  • loose connections
  • bad terminations
  • missing/wrong terminating resistors
  • comm wires running along with / parallel to motor leads

I agree some of the errors was from the Cat 5 cables not being shielded. There is no terminating resistors. I talked to AB engineers and they told me to set it at at least 50ms due to the fact the fastest the PF 700 drive can respond is .1 secs. I think that they said something about that the 2-comm-E could not handle the 5ms RPI I do not rememeber where I heard that but I did.

I do not understand how EN Rx Overruns / and missed IO packets could be noise?

I do know that changing the RPI to 50ms made the machine run more reliable.
 

Similar Topics

With this upcoming project, since I am really a "C"/"C++" programmer and *not* a PLC/Ladder programmer, I would like to use Structured Text for my...
Replies
80
Views
26,520
I created a new program task under that I created 2 ladder files. My first ladder does not have the 1 flag in the ladder icon designating it is...
Replies
8
Views
4,247
Is it possible to export a routine programmed in structured text and import it into a ladder routine?
Replies
2
Views
2,899
Hi all, Is there a equivalent function block that do the same as MOV function in ladder? Thanks.
Replies
5
Views
2,352
Hi everybody, Until now I worked only with ladder logic. Now I have a program with function blocks. It looks more complicate, e.g. you have to...
Replies
4
Views
3,074
Back
Top Bottom