Hello everyone,
I wanted to share my findings with getting the new OPC UA server working (I think you might be interested in this JeremyM :ROFLMAO:)
Currently there is little documentation from Rockwell on how to make it work.

I do currently have a ticket open with Rockwell for more information, and will post my findings as I go.

Code:
OPC Notes
	See TechNotes:
		* QA67230 - Basic Information on OPC UA in v36
		* QA67231 - Guide to enable OPC server/client
		* QA67232 - Guide to using OPC client
		
	The following notes are only for the OPC server, I have not started taking notes on the client side yet.
	I have only done testing with the 1756-L81E and 1756-L82E. In my testing, and after a phone call to tech support, I think the 1756-L81E (and other variations that support 0 max OPC nodes) does not support OPC, but it does have the OPC CIP object.

CONNECTION INFORMATION
	OPC Discovery URL: [url]http://address:4840[/url]
	OPC TCP URL: opc.tcp://address:4840
	Supported Connection Modes:
		* Basic256Sha256 (Sign and Encrypt)
		* None (No encryption or verification, Insecure)
		
	Notes:
		* From one of the sessions I was in while I was at Automation Fair, it sounds like the security information and certificate can (must?) be controlled via FactoryTalk Policy Manager. I have not attempted to do this yet.
		
TAG ADDRESSING
	The controller tags are stored in namespace 6, and can be referenced by name.
	Example, a controller tag with the name "TEST" will have an opc address of "ns=6;s=TEST"
	Program tags are referenced with the prefix of "Program:" then the program name followed by a period then the tag name.
	Exmaple, a program tag names "PROG_TEST" in the program "MainProgram" will have an OPC address of "ns=6;s=Program:MainProgram.PROG_TEST"

OPC SERVER CONFIG
	You will need to message the controller to enable or disable the OPC server. 
	This will be maintained after a download, but I recommend using S:FS (First Scan Bit) to initiate the enable message. This will ensure that OPC gets enabled. By default the OPC server/client is disabled.
	
	To send the message, you will need a struct with the configuration information. The source buffer of the message is an array of configuration information based on the number of TCP/IP instance objects that exist in the controller (AKA: The number of ethernet ports the controller has). This means that on the 1756-L8xE controllers you will only have a single configuration entry, and on the 5069-L3x controllers you will have two configuration entries (I have not tested on a compact yet, so I am unsure how it would handle setting the config info on the third TCP/IP instance used for DLR control.)

	The OPC Config struct is:
		[UINT]  - TCP/IP Instance ID (This is the TCP/IP instance that you are enabling or disabling OPC support on)
		[USINT] - OPC Server Enable (0 = DISABLE, 1 = ENABLE; This will enable or disable the OPC Server on the TCP/IP interface)
		[USINT] - OPC Client Enable (0 = DISABLE, 1 = ENABLE; This will enable or disable the OPC Client on the TCP/IP interface)
	Note:
		* Currently TechNote QA67230 states that it is invalid to operate the controller as both a server and client
			BUT: The message will throw Status 0x0009, Ext. Status 0x0000_2103 if both the server and client are not enabled and disabled together.
	
	The message uses an array of these structs with a UDINT size prefix.
	
	The message configuration is as follows
		Service 0x10 (Set Attribute Single)
		Class 0x3C1 (OPC)
		Instance 0x01 (Default, and maybe only instance?)
		Attribute 0x01 (OPC Configuration)
		Source Buffer: (8bytes on ContolLogix, 12bytes on CompactLogix)
			[UDINT]       - OPC Config Struct Count
			[OPC Configs] - Array of OPC Configs
		Recv Buffer:
			N/A
		Message will return status 0x00 when config is valid.
		Message will return status 0x0x10 ext. status 0x0000_2102 on 1756-L81E controllers as these controllers do not support OPC
		Message will return status 0x0009 ext. status 0x0000_2103 on for an invalid OPC Server/Client conbination
		
NODE COUNTS
	WARNING:
		* If you excede the max nodes, then all nodes are removed from the controller!
		
	Different Controllers support different numbers of nodes, each node is an OPC tag.
	Every tag that has OPC enabled on it counts as a node.
	Every element in an array also counts as a node, plus the base tag of the array
	Every member in a struct also counts as a node, plus the base struct tag (this also applies to sub-structs and sub-struct base tags).
	
	Control/Guard Logix 5580
		1756-L81E  = 0 nodes (OPC not supported)
		1756-L81EP = 0 nodes (OPC not supported)
		1756-L81ES = 0 nodes (OPC not supported)
		
		1756-L82E  = 600 nodes 
		1756-L82ES = 900 nodes 
		
		1756-L83E  = 1200 nodes 
		1756-L83EP = 1200 nodes 
		1756-L83ES = 1500 nodes 
		
		1756-L84E  = 10000 nodes 
		1756-L84ES = 15000 nodes 
		1756-L85E  = 15000 nodes 
		
	Compact/Guard Logix 5380
		5069-L306ER  = 0 nodes
		5069-L306ERS = 0 nodes
		
		5069-L310ER  = 300 nodes
		5069-L310ERS = 300 nodes
		
		5069-L320ER  = 300 nodes
		5069-L320ERS = 300 nodes
		
		5069-L330ER  = 300 nodes
		5069-L330ERS = 300 nodes
		
		5069-L340ER  = 600 nodes
		5069-L340ERS = 600 nodes
		
		5069-L350ER  = 600 nodes
		5069-L350ERS = 900 nodes
		
		5069-L380ER  = 900 nodes
		5069-L380ERS = 1200 nodes
		
		5069-L3100ER  = 2000 nodes
		5069-L3100ERS = 4000 nodes

PERFORMANCE TESTS (1756-L82E, I don't have anything larger to test on)
	Unsecured - Static Values (REAL) - 1 sec scan
	Nodes	Comm %
	0		1
	10		2
	600		2

	Unsecured - Moving Values (REAL) - 1 sec scan
	Nodes	Comm %
	0		1
	10		2
	600		5

	SignAndEncrypt - Moving Values (REAL) - 1 sec scan
	Nodes	Comm %
	0		1
	10		2
	600		6
	
	Notes:
		* In these tests, I ensured that there were no other communications to the controller. Based on this, I imagine that when used with a standard CIP connection getting tag data, and on larger controllers with more supported nodes, performance may need to be closely monitored.
		
		* TechNote QA67230 states that when the Comm % gets too high, CIP traffic will be prioritized over OPC, and the controller will drop OPC requests if necessary.
	
UNDOCUMMENTED MESSAGES:
	Notes:
		* From what I can tell, setting attribute 1 (config attribute) and getting any of the attributes can be done without a licensed connection and will not give a privielge viloation error when sent from a remote device.
		
		* The controller webpage is using these CIP attributes in the OPC object to get this data. You can view the webpage under Diagnostics/OPC Unified Architecture Diagnostics.

	Get current OPC configuration
		Use a Get Attribute Single on Attribute 1 to get the same array of opc config structs that is used to set the config. This can be useful to verify the config on the controller.
		
		Service 0x0E
		Class 0x3c1
		Instance 0x01
		Attribute 0x01
		Source Buffer: N/A
		Destination Buffer: Array of OPC Config Structs (8bytes on ContolLogix, 12bytes on CompactLogix)
		
	Get current used OPC nodes
		This will indicate the used nodes, just like from the controller webpage.
		Use a Get Attribute Single on Attribute 3, it will return a UDINT of used nodes.
		
		Service 0x0E
		Class 0x3c1
		Instance 0x01
		Attribute 0x03
		Destination Buffer: UDINT of currently used OPC nodes
		
	Get max OPC nodes
		This will indicate max supported nodes on the controller, just like from the controller webpage.
		Use a Get Attribute Single on Attribute 2, it will return a UDINT of max nodes.
		
		Service 0x0E
		Class 0x3c1
		Instance 0x01
		Attribute 0x02
		Destination Buffer: UDINT of max nodes supported
		
	Get nodes per second
		This will indicate number of nodes being read from the controller per second, just like from the controller webpage.
		Use a Get Attribute Single on Attribute 4, it will return a UDINT of nodes/sec.
		
		Service 0x0E
		Class 0x3c1
		Instance 0x01
		Attribute 0x04
		Destination Buffer: UDINT of nodes/sec

I hope this is useful

~Trevor
 
Last edited:
UPDATE:
Rockwell has updated TechNote QA67231 to fix the broken images and add the missing logix import files.
 
Just to document some node counts for commonly used tags:
PID_ENHANCED = 166 Nodes (Yikes!)
PID = 69 Nodes
TIMER = 6 Nodes
COUNTER = 8 Nodes
FBD_TIMER = 13 Nodes
TOTALIZER = 46 Nodes
DISCRETE_2STATE = 42 Nodes
DISCRETE_3STATE = 74 Nodes


I will also note, RA has responded to my ticket, the 1756-L81E (and other controllers that support 0 nodes) do not have any OPC support (server or client) at this time.
 
So effectively they still don't have an OPC UA implementation to speak of... there's just some homework from the Summer internships dropped in this version of Logix and hopefully by version 40 we'll have something that Siemens and others have since early/mid 2010's... sounds about right.
 

Similar Topics

Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
Replies
1
Views
86
Hello, I have two 16 point input cards and 1 16 point output card showing module faulted on my IO tree in Logix Designer. The fault code is...
Replies
7
Views
216
Hello, My associate and I are trying to sync up two ControlLogix racks (7-slot chassis) with identical modules. We are able to see the secondary...
Replies
4
Views
197
Trying to setup a message read via Ethernet. I have the path setup as 1, 1, 2, 192.168.66.10 I get an error code 1, ext err 315. I am beating...
Replies
9
Views
233
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
Replies
2
Views
96
Back
Top Bottom