controlnet add device powerflex 4M VSD
Stan Zout__
May 2017
galaxy far far away
I have to add a powerflex 4m VSD onto a controlnet network, at the moment we have a powerflex 40 with an controlnet comm's card 22-comm-c attached with the controlnet daisy chained off, I have set up the drive with a port number and connected it inline but I cant add it into the list as per my attached pic,???
Welcome to the Forum!
I dunno about 'List' definition in your galaxy...
Here on Earth, one programatically adds a device on a ControlNet network using RSNetworx for ControlNet.
Do you have the software? Do you have the CNet current application file?
Add the new VFD to the existing RSNCN file Scanlist using a unique node number not lower than the existing lowest;Save; Re-Schedule the network; Download to the Scanner/Bridge; Save.
http://literature.rockwellautomation.com/idc/groups/literature/documents/gr/cnet-gr001_-en-e.pdf
For a multi-drive application use the info/instructions from within Chapter 7 of http://literature.rockwellautomation.com/idc/groups/literature/documents/gr/cnet-gr001_-en-e.pdf
I believe the last daisy chained drive needs a 120 Ohm 1/4 Watt resistor across the AK-U0-RJ45-TB2P Terminal Block Connector.
There will be a 50ms delay in addition to the CNet NUT to any data packet to/from the each daisy chained VFDs.
I still think you need to re-schedule the CNet node even if in 'multi-drive' mode off an existing node.
Hi, we need to add some ControlLogix IOs to a remote rack via controlnet, based on the info from Ab, Lodix V15 could do it on line, there are...
3,470
Hello, The Facts: 1. I need to add a 1794-IB16 to a controlnet 1794-ACN15 module. The module currently has only an analog input card 1794-OE4...
3,826
Hi All, I have three rack3 I/O in controlnet and plants is running, for some reason, I need add additional two rack2 into controlnet online(no...
1,919
I have had to add a card to an existing system. From the "word I got", all I had to do was add the card using the controlnet software editor, and...
3,049
We are using CLX5K L63 PLC(v15) with distributed FLEX IO Is it possible to add New IO Module (New Flex node) without stopping the controller? Thanks
3,306