Controlnet connection for 1788-CN2DN?

wilsonzhu

Member
Join Date
Jan 2008
Location
vancouver
Posts
278
Hi,

One of my project, use three 1788-CN2DN Controlnet to Devicenet linking Devices, each connect to about 20 Devicenet nodes, and we have about 5 Racks I/O. Because we use 1756-CN2 as Controlnet Scanner, its maxmium connection is 100, I am wondering how may connections of one 1788-CN2DN count? Thanks,
 
On ControlNet, the 1788-CN2DN uses either 1 or 2 CIP Connections. I don't remember if the Status connection counts as a separate connection or not. If you browse through it (which you will for configuration, etc), account for one temporary explicit Connection too.

It does not create a Connection for every DeviceNet slave.

I don't think the 1788-CN2DN can bridge CIP Safety connections... if you are using CIP Safety, there are entirely different capacity rules.
 

Similar Topics

Hi, We have ControlLogix installed at my plant with Flex IOs communicating with controller through ControlNet module. Yesterday, while controller...
Replies
0
Views
492
Hi, I have a big project which has 6 17-slots Racks connected by Controlnet. How much the maxium scheduled Controlnet connection? If I use comm...
Replies
4
Views
2,042
Hi all, I have a Controllogix project, I added some DI/DO, AI/AO card online using unschedule connection.For DI/DO Comm Format: Rack...
Replies
5
Views
6,186
I have a question regarding C-Net topology and device number limits. At the moment, I am counting the number of "connections" (not sure...
Replies
5
Views
10,157
Trying to perform scheduled ControlNet connection between 1747-SCNR/A FW Rev 1.4 and 1756-L55/A !756-M12/A Revision 12.25. Following example in...
Replies
0
Views
4,107
Back
Top Bottom