Contrologix CIP message to a faulted processor?
MajorFault
Nov 2007
Louisiana
36
I have an application where I am doing a MSG read from "PLC_A" reading "DINT_1" in "PLC_B". What happens if PLC_B faults? Will the MSG read still perfom without error in PLC_A, continuing to read the "last state" data? Or, will the MSG read instruction error out?
If the reason for the fault does not clear the user program (like a hardware watchdog error) then the controller should reply to messages despite being in a Major Fault state.
I can give this a try at the office tomorrow to verify that.
Another way to exchange data is to use a Produced/Consumed Tag. You can then use a GSV instruction to read the Mode of the remote processor and can use it to decide whether to use the Produced data or not.
Thanks for the info. I tested this in the shop today and indeed if the remote processor faults the local message instruction will continue to opearte as normal.
Can you do produced/consumed over ethernet? I have used them alot before but, always over ControlNet.
Thanks again
We have several machines using a master/follower type control using Pflex 700 drives with each one having encoder feedback to both the drive and a...
3,962
Can anyone confirm that using contrologix 5580 controller is not possible to work with powerflex 527? It's been a couple of days now that i am...
1,192
Hello, I have a flow control PID that keeps locking up. It seems to control fine but after a while the output no longer moves. For instance...
968
Hi everyone, I can't add any modules to the Controllogix backplane and it doesn't matter online or offline. Both is not working. Please see the...
2,992
Hello, I have a question regarding the possibility of using messages instructions to communicate between: PLC5/80E Series D - CE Water Mark...
3,064