Contrologix - RsLinx cannot communicate. Batt LED flashing Red.

bigLee

Member
Join Date
Jun 2018
Location
Florida
Posts
77
I have a 1756 L62 ControlLogix5562 controller I cannot connect to via ethernet. Get RSLinx cannot communicate message. Verision 19.

It has a battery solid red LED and flashing red OK led. I know that is a recoverable major fault. Will this prevent me from connecting via ethernet?

I am going to try serial 232 connection next week. I've been tasked with upgraded to a L81 E contrologix version 30. I do not know if I have the most recent project or not. Ideally I would upload from controller, get the new controller set up and just swap.

Just curious as to why I can't connect and if I will be able to. Any ideas always appreciated.

Thanks,
Ben
 
The LEDs as you describe them would be normal for a dead or missing battery.

I have a 1756 L62 ControlLogix5562 controller I cannot connect to via ethernet

What does that mean? Can you see the Ethernet module on your Ethernet network? Can you get through the Ethernet module to see the Logix chassis in RSLinx? Can you see the L62 or other modules?

And stupid question here...are you using RSLogix 5000 or Studio 5000? And what version of software? Do you know the firmware version of the L62?

Screenshots help immensely.

OG

p.s. While a flashing red OK indicator almost always indicates a recoverable fault, it can in some instances actually be a non-recoverable fault (which is usually solid red).
 
Last edited:

Similar Topics

Trying to open an old project It was Fix32 talking to a Contrologix L61 using Rslinx. I can not remember the ABR 7.x OPC driver setup and...
Replies
5
Views
2,518
Can anyone confirm that using contrologix 5580 controller is not possible to work with powerflex 527? It's been a couple of days now that i am...
Replies
8
Views
1,190
Hello, I have a flow control PID that keeps locking up. It seems to control fine but after a while the output no longer moves. For instance...
Replies
4
Views
967
Hi everyone, I can't add any modules to the Controllogix backplane and it doesn't matter online or offline. Both is not working. Please see the...
Replies
13
Views
2,991
Hello, I have a question regarding the possibility of using messages instructions to communicate between: PLC5/80E Series D - CE Water Mark...
Replies
12
Views
3,063
Back
Top Bottom