Convert 0-10V / 2-10V signal to 0-20ma or 4-20ma
Siemens do some interface relays - their codes 3RS17001CD00, 3RS17051FD00, 3RS17051FW00 +others. If you use RS Components then their part no. 418-4843 would do. (page 1-1223) - hope this helps?
I don't think that resistor works now. There is also input resistance which comes to series with 500 ohm, so eventually current is something else than 4-20mA
Maybe it works with 513 Ohm resistor for 19.5mA. Rest 0.5mA goes to Belimo when output is 20mA and voltage is 10V?
10V/20mA = 500 Ohm resistor between 20mA input and Belimo.
Test 1'st and measure current!
You've got to be careful with this. Most voltage outputs expect the resistance on the output to be quite high, typically 1,000 Ohm or more, and the current to be quite low. Putting a 500 Ohm resistor may draw more current than the output can handle and fault the output. The resistor trick works well going the other way - getting 4-20 mA to a voltage input, but not backwards.
A lot of companies make signal conditioners to go from voltage to current, and this is how I've always done it. For example:
http://www.automationdirect.com/adc/Shopping/Catalog/Process_Controls/Signal_Conditioners/FC-33
You are Correct, must be careful!
In my example output is 4-20mA and Belimo input needs 2-10V.
Max resistance is 500 ohm for Simatic Analog Out with 4-20mA signal as in my example, so it works. If max resistance is bigger, analog voltage mast get dividing the resistance as trimmer. Mostly max. resistance depends of analog output unit power voltage.
Same Siemens Analog output unit voltage mode output max load is 1kOhm as You mentioned. But problem is how we can use 4-20mA output signal for 2-10V Voltage input signal. Usually everything is possible, it is only Ohm's law. :D
Interface Module 2...10V Converting Into 0...20mA Or 4...20mA
Hi AANZ,
To make a coversion form 2...10V into 0...20mA or 4...20mA, I would suggest using an interface module, like for example offered by Turck.
A detailed description of this module can be found here: http://pdb.turck.de/media/_en/Anlagen/Datei_EDB/edb_7506323_gbr_en.pdf 🤾
and also here: www.turck.com
When you would like to order it consider visiting my website,
and clicking on the link for PLCcenter Industrial Store, you will see it in the third collum of this page: http://www.industrial-automation-hands-on.com/help-an-engineer-out.html
Always take care! 🍻
So in the past I have converted a 4-20ma signal to 0-10v using a 500ohm resistor. I am attempting to control a Johnson Controls damper motor with...
1,578
Hi, i want to convert 0-10vdc output to 4-20ma signal.
3,239
Hi, I have a MicroLogix 1100 PLC, and it has two 0-10v analog input channels. Is there a way to convert a 4-20 ma loop powered device for use with...
26,070
Have a question. Have a transducer that gives a 0-10v output. Is there a way to add a resistor so that it would appear as a 4-20ma signal?
23
54,426
I'm trying to find an analog conditioner to convert a 0-10 V signal to a +/-10V signal and not having much luck. Has anyone ever come across a...
2,070