Convert Klockner Moellier PLC to Click PLC
Maxbeers
Sep 2007
Amarillo, TX
I am replacing an older Klockner Moellier PLC with A-D Click PLC.
It was not until the end of the ladder I found that there are Jump instructions being used.
Click PLC does not have "jmp" instructions.
I am looking for a way around this.
As always any help is appreciated
Use the original JUMP enable logic to condition the rungs to be "jumped" and "clean-up" the rest of the ladder making sure every bit of it is efficient and necessary.
You might run into "scantime issues" since the JUMP/LABEL pair is being used for decreasing the CPU burden, however, I have seen it done since you are using a much "younger" processor.
Compare the scantimes of the two CPUs running "the same" application file if possible; less than 10-15% increase should be acceptable.
the easiest way is to use subroutines, as most jumps only jump over a few instructions. be aware that after a jump there is mostly another jump to go back to the original program loop.
so you can treat the second jump as a return.
start your subroutine by a compare.
Hello all, I'm currently working on a servo motor linear positioning system (ball screw). I'm all set up regarding communication between my HMI...
112
I have an application using an incremental encoder and then I convert it to degree (0-360) using calculation program. For a while, the calculation...
365
Hi all. Me again still learning Rockwell. So I'll be polling an INT data array from a Modbus SE power meter with a L82 (with a Modbus ProSoft in...
56
1,475
Hello, could someone kindly convert the attached RSP files that are currently used for SLC 5 PLC into PDF please
557
I'm trying to convert an RS Logix 500 fille when I open the 500 file and try to "save as" a .slc file, it does not allow it. It says " SLC library...
721