Hi All,

I am looking to see if anyone has had this issue before.

I have a TIA portal on site which is programmed in TIA Portal V13.0 but the firmware of the CPU is V4.1.

When I try to upload using TIA portal V13.0 I receive an error when uploading the hardware config.

I cannot add the CPU with Firmware v4.1 only 4.0 which I think is the issue.

I used a TIA portal with V13 SP1 which allowed me to add V4.1 of the firmware but when uploading it stated the program was created in an earlier version of TIA portal.

I am stuck at the moment as I believe the software is written in TIA portal V13.0 but the firmware of the CPU seems to indicated i need SP1 installed.

Has anyone had this problem before.

Thanks in advance
 
Maybe there is difference in Upd XXX version of TIA 13 SP1. I saw on Siemens forum that fw 4.1 needs V13 SP1 Upd 1. Check your version of SP1. I guess difference in Upd should not be so critical, but it is TIA Portal (who knows) ....
 

Similar Topics

Hi All, I am trying to communicate siemens PLC with FESTO Servo & 3 Festo make Steppers on FHPP Modbus Protocol. Sometimes, I face Modbus...
Replies
0
Views
1,339
I have a siemens CPU 1214C PLC and a Siemens TP900 HMI connected via Ethernet. The HMI is only for setting up - when I disconnect the HMI the PLC...
Replies
1
Views
1,498
Hello all, I have a one problem. I would like to upgrade Mitsubishi PLC Q02 to Q03UDVCPU. I have Q02 program and I change to PLC type and try to...
Replies
5
Views
118
Hello everyone! I need to connect to a DL205-1 CPU and, as far as I know, I need to use DirectSOFT 6 software for the connection. Is anyone...
Replies
1
Views
67
hello s7-400h and wincc are connected to each other via Ethernet. I need help on how to do time synchronization
Replies
0
Views
54
Back
Top Bottom