Cpu 318-2 dp issue

Hello sigmadelta,



The crane manufacturer tells me to check the Profibus cable / connectors ....

I have performed the reset of the plc as your procedure without any success.


So while waiting to receive the profibus cable as well as the connectors, during a verification, the analog input card 6ES7 331 7KF01 0AB0, has a low voltage output (21.4VDC to 22VDC max) for the supply of the sensors ... but this card is well powered 24VDC ...



Is this power supply of the sensors able to generate the disturbance in the Profibus network and my breakdown without the SF leds being lit ?

Any idea of ​​how the shunte/test or from where can the anomaly come (defective internal resistance?)

thank you in advance
 
You don't actually need to wait for the profibus cable to test.
Just use any cable with at least 2 conductors.

In some case just move the HMI to close to CPU and use a short profibus cable to test.
 

Similar Topics

Hello all. I have some problems with the Load Memory RAM on a Siemens S7 CPU 318-2 (6ES7 318-2AJ00-0AB0 fitted with a 512kb flash MC 6ES7...
Replies
6
Views
6,826
Dear Friends, I have a S7 300 (318-dp 2)P.L.C. I need to connect a touch panel TP 270 via wireless radio modem. My problem is the transmission...
Replies
2
Views
4,107
Dear All After complete power off, when we tries to power on the PLC (CPU 318-2 DP) some times it lost its user program also system data. Then we...
Replies
2
Views
2,981
Hello, We would like to replace the normal rack of our PLC to an active bus rack. We have a CPU-318-2Dp and some digital and some analog cards...
Replies
2
Views
2,816
I Forgot Password,i Want To Download The Programe From Pc & Change The Password.suggest How To Erase Memory In The "flash Card" Of Cp 318.
Replies
2
Views
5,417
Back
Top Bottom