Ok, I found the error, it was the DIP Switch. Now I can program the PLC with the CX-Programmer fine.
Thank you Paulus and Gtsuport, in the future I will only have programming questions :) :D
Hi guys, i have the same problem. Failed to connect.
I have CQM1H-CPU21 im using C200HS-CN220-EU cable.
What could possibly wrong with the set-up.
Lot No. 03681
currently im trying it on my laptop, using standard USB-SERIAL HL-340 cable. Since my laptop got no serial port.
Your problem is RTS/CTS handshaking.
Your cable is set to require that handshake, you need to modify the cable to ignore the handshake, like the link I provided.
You will need to short pins 4 and 5 together on the PLC side.
Also short pins 7 and 8 on the PC side.
I use the cable diagram from the posted link to the DB9 port. I do not have the CQM1-CIF02 cable.
See attached pdf file.
is this same with CJ1M-CPU21??
PLC DB9 pinout is the same for CQM1 and CJ1M.
Also check the dip switch settings on the cpu.
Information is located in the W339 manual.
Hope this will help.
Hi everyone, I need to upload 2 Omron PLC programs from those PLC's: CQM1 CPU21 and CJ1M CPU22. On my laptop I have just USB ports. I have...
2,976
Hi All, I am using the OMRON CQM1 CPU21 to measure the machine downtime and do some calculation and display in the FactoryTalk View SE (Computer)...
5,546
is this the input for the PLC? and may i know what is the channel for the OD212(Output card)? thanks =)
2,081
Hello again dear friends. We have a couple of machines in our plant that we want to modify.We would need 16 more inputs and a couple of...
1,422
I have never worked with an Omron PLC. I have a CQM1 CPU21, CX Programmer version 2, and a CQM-1-CIFO2 communication cable. What is the step by...
2,879