Curious: What if I copy a PID tag to another PID tag in RSL5000
wildswing
May 2005
Sault Ste Marie, Ontario
281
Just curious, trying to make set up of 20 PID tags identical. What if on first scan I
COPY MyPIDtag01 to MyPIDtag02 Length 1
COPY MyPIDtag01 to MyPIDtag03 Length 1
COPY MyPIDtag01 to MyPIDtag04 Length 1
etc...
Tags are all PID type. Is that legal? It does seem to work. Beats opening each occurrence and typing everything in. This is just to get stuff set up initially. No plan to leave it in long term. I have other plans for changing PID values later.
This way I set up the first, then it's values all get copied to the other 19. All loops are physically identical.
I tried:
COPY MyPIDtag01 to MyPIDtag02 Length 19 but no go.
Excellent.
Your last reference wouldn't work in two ways.
The COPY would only have worked if you were copying a block of 19 contiguous PID tags into another block of 19 contiguous PID tags.
And your nomenclature doesn't show an array [] mark so there is no guarantee that, even though they have sequential numbers, that they are contiguous in memory.
Excellent.
Not being facetious there are ya Bernie? ;)
šŸ™ƒ I new that. o_O
You're right. It's not an array. Each PID tag is a single tag...NR01_PID, NR02_PID, NR03_PID...
I have a client who periodically experiences network communication issues. Sometimes when I VPN into the site, their SCADA systems will flash comm...
194
I'm focusing on Rockwell programming for a couple of projects, and I've been thinking about some of the details I've come across while working...
2,356
Hello all. I was starting to get into a new project (that will probably never see the light of day because $$$) at the plant I work in and...
26
5,603
Just curious, Have you noticed how the Honeywell C200 and the A-B Controllogix look alike? Are this two related somehow? Are they compatible...
2,044
Studio v31 FTV v10.01 Found the logic was acting backwards. so I switch the name plates on the three way "Control Mode" Right is the FactoryTalk...
1,533