Current Transducer
arroyo said:
I'm looking for the correct size CT (current transformer)
I want to install (1) CT to monitor the amps of one leg of a 3 phase 460 volt 125 HP motor with a full load amps of 167. I have an analog ampmeter scaled from 0 - 150 amp, and a CT with a 300 to 5 ratio. , please advice if this will work, or do I need to make some changes.
thank you for your help
Lessee now
You have a motor whose full load is 167 amp.
You have a 300 to 5 CT
You have a meter whose scale is 0 to 150 amp and I ASSUME is set up for a 5 amp input.
Now if I am right then the meter would work BUT it will not read correctly - would only read at one half the actual current.
What I think you need is a 0 to 300 amp meter matched to a 300:5 amp CT. This would actually be better because you would not wrap the needle during starting.
Dan Bentler
I have a Pump 1 Current in my Local:5:I.Ch00Data address. I need to add this to my ladder logic program as the goal is to have it eventually be a...
1,473
I purchased a 4-20ma AC Current Transducer, it can be set to 0-100a, 0-150a, 0-200a. It is not True-RMS. This is connected to a panel meter and I...
1,487
Hello, I have a 2 wire, 0-10vdc output, self (not loop) powered current transducer from NK Technologies that's giving me incorrect values when I...
2,651
I need some help with wiring a DCT200-42-24-F DC Transducer to a AB 1769-IF8 Analog Module in a CompactLogix PLC. I thought it would be pretty...
4,740
Does anyone know if i can use a current transducer to tell if a 3-phase pump is running dry. I have done this before with a Franklin Pump Saver...
3,216