I need some help with wiring a DCT200-42-24-F DC Transducer to a AB 1769-IF8 Analog Module in a CompactLogix PLC. I thought it would be pretty straight forward being only 4 wires but I must have missed it somewhere because I cannot get any output from it.
The 1769-IF8 does not provide loop power, so you would need an external power supply to provide the current for you. I took a look at the DCT200-42-24-F spec manual, and towards the end of the spec manual it shows you how that's wired link is below
http://www.automationdirect.com/static/specs/acuampdct.pdf
now as you can see on that schematic terminals 1 and 2 are going to be wired to your external power supply, im assuming you would use a 24vdc power supply, then terminals 3 & 4 is your 4-20 mA signal output that should be wired in to your 1769-IF8 Analog Module.
Here is the manual link i found online for the 1769-IF8 Analog Module.
http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1769-in067_-en-p.pdf
go to page 8, 9 & 10. Make sure you follow what it says especially on grounding properly and wiring correctly.
That should be all you need.
I have attached a diagram of sorts showing how I currently have the transducer connected and I have circled the connection points. Is this correct?
The spec on your transducer says its output is 4-20ma. You have connected it the voltage input on the input card. Move the wired labeled #4 to terminal "I in 0+" on the input card.
Has anyone successfully connected a 1785-KE 15 pin serial port to a modern radio RJ45 port using 3 wire standard Tx,Rx,Gnd? No Handshaking? I am...
1,559
Is it OK to run the Neutral wire thru a disconnect switch for a electrical control panel as shown below? If not, can someone elaborate as to why...
20
7,894
Hi, Calculation of voltage drop of a 2 wire transmitter connected to plc AI is pretty simple and straight forward. My Question is could you...
2,138
Hey, We have a 3-wire 4-20mA sensor that is connected to a display like this Now i need to connect this to a siemens ET200S analog input...
2,929
how to connect three number 4 wire transmitter to analog card IF16 1756 plc
3,266