how to connect 4 wire transmitter to allen bradelly plc1756 if16
sir it is accelerometer sensor , company Forbes Marshall dual channel VIB TRANS (VIB-T ll). Model : VIB-T-ll-A-P-V-VELOCITY-0-1020-1-1-0
Mr. Mickey I have 16 transmitter in field all are of same type that i mentioned above post.
And as your attached drawing here in my plc all iRTN 0 to iRTN 15 are loop together and loop to RTN. Now for transmitter number 1 is connected to IN 0 (+) and iRTN0 (-), transmitter number 2 is connected in IN 1 (+) and iRTN 1(-)
Number 3 connected in IN 2 and iRTN 2 viceversa. Is it correct.
Yes you are correct, because you are connecting the sensors as Single-Ended current.
channel showing wrong feedback in allen bradelly PLC 1756 AI Card IF16
Sir, here i face a problem that the signal come from first instrument(4 wire transmitter) is connected in IN0 and iRTN 0 Second on is connected in IN1 and IRTN1, Third is Connected in IN2 and iRTN 2 and all iRTN is connected in RTN. then when signal comes from First Instrument is also showing same feedback in IN2.
Since the sensor is active, try this:
+ of sensor to iRTN-0
- of sensor to RTN
IN-0: Not connected
Remove jumper from iRTN-0 to RTN
The other 2 wires go to the 24VDC power supply
I´m a Siemens, not an Allen Bradelly user.
Hi, Calculation of voltage drop of a 2 wire transmitter connected to plc AI is pretty simple and straight forward. My Question is could you...
2,146
Has anyone successfully connected a 1785-KE 15 pin serial port to a modern radio RJ45 port using 3 wire standard Tx,Rx,Gnd? No Handshaking? I am...
1,562
Is it OK to run the Neutral wire thru a disconnect switch for a electrical control panel as shown below? If not, can someone elaborate as to why...
20
7,952
Hey, We have a 3-wire 4-20mA sensor that is connected to a display like this Now i need to connect this to a siemens ET200S analog input...
2,940
I need some help with wiring a DCT200-42-24-F DC Transducer to a AB 1769-IF8 Analog Module in a CompactLogix PLC. I thought it would be pretty...
4,743