These instructions compare two sets of BCD date and time data each three words long and produce a true or false result. What are you trying to do??
I'm having trouble understanding this too.
Using a CP1L-EL20DR-D.
I'd like an output relay to switch on at midnight.
So far I've figured out:
C = 38 (which is 000111000 to HEX)
S1 = A351 (the internal clock)
S2 = ?
How do I input 0000 hours into S2? Do I use MOV into an address like D100? If so, how?
I'm trying to understand the conversion between digits to binary or whatever data is required.
Ok I got it working after 8 hours of trial and error..
For anyone who's struggling like me:
C is the mask for the timer and lets you ignore part of the current time.
The bits correspond to year/month/day/hour/min/sec.
So if you only need the hour it'll be 000100, or 3B in hex.
MOV #3B into D0 and that will be your mask.
S1 is the current time.
A351 = MMSS (minutes/seconds)
A352 = DDHH (day of month/hour)
A353 = YYMM (year/month)
S2 is the hour you'd like to set
So for 2PM you'd put #1400
I hope this helps and please correct me if I'm wrong.
Use ANDW #00FF or #FF00 to mask the values you do not require. For hours use ANDW #00FF A352 D???? and hours will be placed in D???? Quite easy when you know. The #00 masks the days. It is a 24 hour clock so 2PM is 1400 as you suggest but is in HEX. To compare use = D???? #14 then an output bit and the bit will turn on when it is 2PM and off at 3PM.
so the CIO is for I/O and the W0.00 is like Siemens M 0.0 What is comparable to Siemens DB? I usually Map Siemens External I/O to a DB and then...
2,023
Has anyone done SMS messaging from an Omron CJ2J-CPU31 PLC? If so could you help please. Omron here in Oz have not had any experience doing this...
174
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
64
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
110
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
261