DA70A ModBus TCP/IP Slave Communication
hoguegregplc
Aug 2023
McKinney, Texas
CR3000 HMI ModBus TCP/IP Master has gotten erratic after increasing block size to 24 at DA70A in Protocol 1. What should a practical guide be for block assignment? Will splitting into dual Protocols help?
Welcome to the PLCTalk forum community !
Please clarify: is your DA70 initiating the comms to a "slave" peer, or is it answering requests from another device ?
Can you describe what you consider to be "erratic" ? Is the reply time changing, or is your client seeing a timeout ?
24 registers should be trivial to read or write with Modbus/TCP.
What kind of device is the other device ?
What i found was that I completed the 40000 mapping of Data Tags in the Communications protocol of the DA70A to match all of those entered in the CR3000 Data Tags, and the erratic display at the CR3000 has been eliminated.
I did not think the Communications protocol omission at the controller would interfere with the HMI, but I no longer can duplicate the error seen (failed button actions, numeric displays flashing blank) with the 40000 registers unassigned. Would this mapping correction really fix a problem?
Build error occurs with TON ladder logic command. Time Input expected on block. Using Integer Tag under Control Local, and then hard number 19...
759
Hi Everyone, i was hoping for a little help with this module. i have data that needs to be read from a different plc through the Modbus plus...
227
I have a PH meter that I am trying to bring its data into 1756-L81. I have downloaded the Rockwell MODBUS AOI kit, but I am not sure if I need to...
167
Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
48
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
222