Danfoss FC300 controlled over profibus

recycled_mind

Member
Join Date
May 2007
Location
Cebu, Philippines
Posts
118
Hello experts,

Maybe anyone of you who has experience working with Danfoss FC300 controlled over profibus, please share.
My problem is controlling in reverse direction.
I made a successful start and stop command and setpoint using PPO type 6.
Now, I want to control it in reverse direction.

I move HEX value of 847C to PQW256 but it will not turn on the motor in reverse direction. the motor will just have a humming sounds ready to turn. but when I move setpoint to the MRV (PQW258) it seems the VFD cannot run with postive setpoint in reverse directions.

Please help. Do i forgot something in the configurations?

Regards,
AlexS
www.watchdogautomation.com.ph
 
Hi Recycled_mind!

Did you remember to set Par. 4-10 to "Both directions"?

Do you need both bus and digital control or do you only control over bus? If you need only bus, I'd set Par. 8-01 to "Controlword only".

If you also need digital control you need "Digital and ctrl.word". But then I'd check out Par. 8-5x. My FC102 would not reverse but ran forward (on both 047C and 847c), it was because Par. 8-54 was set to "Digital input".

Best regards,

Michal_dk
 

Similar Topics

I want to read voltage and current from a Danfoss drive FC300 with S7-300 PLC. I need help with the programming. Hardware bit has been done by OEM.
Replies
15
Views
6,527
Hi I have little problem figuring out problem with this drive. Resistance between earth and phases is about 7Moms, is it enough? When problem...
Replies
27
Views
17,054
Can anybody point me in the direction of a manual/insructions for using the smart logic functions on this inverter. I have a simple pumping...
Replies
0
Views
4,509
Hey guys. As the title suggests, I need to configure a Danfoss Aquadrive FC202 inverter, so that its logic inhibits the local command when the...
Replies
2
Views
48
Hi all, We are currently experiencing an DC over voltage fault on one of our inverters. During commissioning a snag was raised whereby excess...
Replies
0
Views
204
Back
Top Bottom