Detecting loss of connection through RSLinx
welby
Jan 2008
Indianapolis
I am fairly new to Linx/OPC/and PLC's in general, but I've done ok up to this point.
I am writing an application that communicats to the plc using opc via the rslinx sdk. I am looking for the best way to monitor the state of the plc connection. I bascially need a toolbar in my app that will turn red whenever the plc/app communications is lost.
In the past, we have used a heartbeat timer to periodically listen for data from the plc, and confirm the connection with that method. Is this the only way, or is there a better way?
Thanks for the help.
Welby
I like to watch the scan toggle and set an alarm if I lose it, but that's similar to a hartbeat timer.
Charlie
Your heartbeat isn't a bad idea. Simple. Effective.
They might have status tags - that's up to the OPC server. I've used their troubleshooting tools within RSLinx, but I don't know if they have status tags automatically set up - I've never noticed them while browsing the PLC address structure in an OPC client.
You can also tie it to the OPC "quality code". 192 is "good data", go figure...
bernie_carlton said:
Don't the OPC engine have a failure state indication?
RSLinx Classic has some Pre-Defined Objects that provide information on the Server itself and its connection to the controller.
In RSLinx online help, search for the keyword "predefined objects" to see all the objects.
@IsPresent is a pre-defined object corresponds with a "Red X" in an RSWho browse. It used to be that this had to be a PLC-5 controller type but I've used it successfully with an ordinary Logix connection too.
The general syntax in an OPC link is:
=RSLINX|PLCTalk!'@IsPresent'
Good to know - Thanks, Ken. Is there an online reference (from the help) that you could link in?
Thanks for the replies, they all gave me somthing to think about.
The way I ended up going was watching the PLC clock for the seconds. If I do not receive a datachange every second, then I know I lost connection.
Hello all. I am currently using a compactlogix L36ERM to control 5 Powerflex 525 Drives over Ethernet. The problem I am having is determining...
4,211
I had bought a used PLC before but I had to return it. Once in a while its run mode shut off momentarily. I had the PLC on my desk. (No I/Os...
22
5,388
I've been called to a site to assist with an ASi fault. The line has been down for a couple of weeks following a failure of the ASi power supply...
1,315
I am looking at an application where I will need to detect small hairline cracks in stamped metal parts. The sensing will need to be done in the...
1,147
Hello everybody, I am working on a project which has HMI FTView SE 13 (Local) and controllogix L71 PLC. I have a question how does PLC detect a...
516