Device to convert AC input voltage to analog DC output

AB2005

Member
Join Date
Nov 2006
Location
Lahore
Posts
318
Hi;

I need to monitor and log the 3phase AC input voltage for which I need a device to convert AC input voltage (say 350 - 440V) to analog (0-10v or 4-20mA) to connect with PLC. Has anyone used such device? Please share the make and models number.
 
I agree that Power Meters need a different interface, but I have found that the prices have dropped a lot recently.
This is £169.00 with a modbus RTU output:
https://www.smartprocess.co.uk/mid-...tricity-meter-pulse-modbus-smartrail-x835-100
Or to go with a well known make, this is Siemens with a Modbus TCP output:
https://uk.rs-online.com/web/p/ener...ol_Gear_Whoop-_-Energy+Meters_Whoop-_-1809613
From these you can get Voltage, Frequency, Current, Power plus loads of other values.

If you just want one value then 4-20mA is the way to go. If you want more than one value then a bus connected device will give you a lot more data.
 

Similar Topics

I hope this makes sense. I need something that can accept the data from an Excel or csv file and can output a 4-20mA signal to represent this...
Replies
4
Views
2,266
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
Replies
0
Views
60
Hey guys, I have to take an upload of a program on an S71200 PLC to change a hardware config option and then redownload the program with this...
Replies
3
Views
111
Hi, First time poster, long time reader. I've got a mass flow controller device for controlling the flow of gas. It has a flowmeter and an...
Replies
4
Views
276
We are trying to poll data coming from a PLC for remote monitoring we have the IP address of the PLC and the default port number and the path is...
Replies
25
Views
583
Back
Top Bottom